IEC 60598-1:2008 第5章中的要求
5 V- L3 J6 ]/ h* v& \Table 5.1 – Supply cords O+ g/ B+ y, [# f4 l, \ [9 c
Luminaire Rubber PVC+ E# P @8 r$ g. M; a1 |
Ordinary class I luminaires 60245 IEC 89 60227 IEC 526 i; r8 ~8 Y+ C* ~3 r) @
Ordinary class II luminaires 60245 IEC 53 60227 IEC 52
7 {1 |+ I$ ]. Y* P% lLuminaires which are other than ordinary 60245 IEC 57 –% F! v/ w/ b8 ?) h; L
Portable rough service luminaires 60245 IEC 66 –
. D( e v. `* M( u
2 W7 e1 x- b" g7 t! h1 ?6 ~To provide adequate mechanical strength, the nominal cross-sectional area of the conductors4 p! w" j9 Q7 h! [+ E$ ]9 C2 Z5 ?
shall be not less than:% a" K4 ~1 U( L+ @, Q2 e
– 0,75 mm2 for ordinary luminaires;
& \+ h1 ?& O9 V5 T: l+ ^7 V– 1,0 mm2 for other luminaires.
/ ^/ Y4 }' k9 W- D$ [' z) bIf the luminaire is provided with a 10/16 A socket-outlet, the flexible conductor nominal crosssection area shall be at least 1,5 mm2. |
|