39.3 Tests are to be conducted at rated frequency and a test potential not less than 120, 208, 240, 277, 480, or 600 volts as appropriate for the voltage ratings. See Table 39.2. The Temperature Test shall be conducted at a potential between 90 – 110 percent of the potential specified when the load current is adjusted to produce the maximum normal heating.
3 F" x1 u+ ~% _6 N* k. V--------------------------------------------------------------------------------------------------------------------------------------
% Q) x3 V. S/ R# T7 A% x
. h3 _# _( ]; o1 [( MAbove is from UL standard, normally, three points 90%,100% and 110%, then select the max load(output current) case... |
|