| Measured limiting voltage
1 D; M) d D, a- Z | 7.5 a), 7.5.4 a)9 c! [( b/ C* Q: D. ~
| 61643-1(ed.2)
: V% z% b( M/ `( L |
- S5 x0 p$ z: X# lStandard(s)-(year and edition):
' K$ s" D3 B0 q! A3 {IEC 61643-1, 2nd edition, 2005-03" Z! ~3 s/ W- t9 Z' o Z0 [
Sub clause(s): 7.5 a) 7.5.4 a)
f" m9 V2 F/ DDSH- 6437 S) L, A9 r+ r9 u6 n
Subject:* V& R- `5 |! C( c: N) H5 _
Measured limiting voltage
# |7 m: Y r/ F5 mKey words:" Y: B) F0 \- s* J+ s2 J5 q6 k
- measured limiting voltage
, F! g& E8 c7 L. l6 _& u; _- protection level
' }4 ?& E9 ?/ I+ g; {! m# ?- energised testing- S R; H2 W9 E0 E# ~& _
Approved by the 45th CTL plenary meeting 20082 Y/ h' E" _2 o- @: B5 K- _8 X3 J
Question:5 ]4 J5 J* k6 s9 H' I" |3 ], x
Testing of one port SPDs according to test class III (Type 3):
: i' }2 ^+ _0 {9 a' X, @ d2 KShould the test to measure the limiting voltage with the combination wave be performed with the SPD being energised at Uc or without energisation?; j6 y$ }6 Q: A
Rationale:- [9 l' N7 v% B6 F) o/ T
Clause 7.5 a) of the standard requires:
3 ?2 ~% l: V6 I' yAll one-port SPDs shall be tested unenergized. …1 m1 [& h8 m' @7 P* n
Clause 7.5.4 of the standard requires:" }& D, f O$ ` e" J
a) The combination wave will be applied to an energized SPD, with the mains voltage at Uc.
, V2 s, C: ~+ S( aAs testing energised may give higher measurement results, the test should be performed energised8 w! ]- j4 T2 W8 D3 I
Decision:
+ r# B+ U4 s" C( U2 |1 IThe test shall be performed with the SPD being energised at Uc.. N f% Q0 f# _4 X# K