对于电源线——有插头或者尾插的。
+ \' m+ [1 a$ V) }$ o" N: L' }各国的标准的规定:' l: g4 N" n6 o8 P
IEC 60884-1的17.1 The insulation resistance is measured with a d.c. voltage of approximately 500 V, the8 R- j# ]: T# c6 y' ?; e! Y
measurement being made 1 min after application of the voltage.6 F3 t4 ^2 D% `/ d
The insulation resistance shall be not less than 5 MΩ., E0 z j) Q M# `3 b& k9 J" ^
- N* D9 @ }/ @2 ~8 o4 e
GB2099.1 的17.1条款,绝缘电阻5mΩ以上6 K5 w; y' S6 J! ], O) ~
( r* m$ u; x, u3 ]5 J9 I3 @
JIS C 8303 的5.5 絶縁抵抗 絶縁抵抗は,7.6によって試験したとき,開閉試験前が100 MΩ以上,開閉試験後が5 MΩ以上でなければならない。
. c( u5 B! }# g* ]. G
' F# ^' h* N7 jUL 817 的89.1 The insulation resistance of a fitting shall not be less than 100 megohms between:。。。。。。* [5 @6 d# Q. `3 @8 ]5 Z8 q
0 W: g8 m* G9 R: v b Q# kAS 3112的规定:
- Z& ?* C4 V! j2.13.2 Insulation resistance test& b9 G! M" J0 N! c
The insulation resistance of a plug shall be measured at a voltage of 500 V d.c. as follows:3 K- i) }: Z4 `) Q
。。。。。。
6 M. O% ~0 S, \6 e- W# U; lThe measured insulation resistance shall be not less than 5 MΩ. |
|