4.10.1 For metal encased class II luminaires, contact between:4 p2 U+ W# b9 [3 R& }, c
– mounting surfaces and parts with basic insulation only,
" x) g( t' D. |6 c- Z# u– accessible metal parts and basic insulation,
% J& b0 h* N l( x; v4 l( a. C! rshall be effectively prevented.
7 Q, J4 q' z b' X# R; `NOTE 1 This requirement does not exclude the use of bare conductors if adequate protection is provided.: ]' M* k X/ h1 E. U: D: @( e% y3 B
This wiring includes internal and external wiring of the luminaire, and fixed wiring of the4 n0 Q0 x3 K0 O5 P# O" R7 v2 b) p9 n
installation.
+ E5 B) e( d- g! p | iClass II fixed luminaires shall be so designed that the required degree of protection against# V7 P& _' P; }6 G
electric shock is not impaired as a result of the installation of the luminaire, for example by
* W# |0 Z& C' z3 _1 V acontact with metal conduits or metal sheaths of cables.; R- D% J0 {$ M! q/ ~
Capacitors shall not be connected between live parts and the body of metal encased class II1 K6 o I6 |& \- A
luminaires, with the exception of interference suppression capacitors and switches meeting the* L: L- I" p# E* e- B1 F
requirements of 4.8.8 D" Q6 D1 P; N# @; E
The interference suppression capacitors shall comply with the requirements of IEC 60384-14
7 @: a# R* N, I6 U. D: _$ n; fand the method of their connection shall be in accordance with 8.6 of IEC 60065." {+ R" u* ^( i3 H5 ?9 j
NOTE 2 Contact between accessible metal parts and the basic insulation of internal wiring may be prevented by# t8 a8 B$ G R, j! e
sleeves or similar parts which comply with the requirements for supplementary insulation.
- f; F# a) G, ?6 y, JCompliance is checked by inspection.
% N: E- D( q' |) n4 A9 r以上是IEC 60598-1的4.10.1部分,没有你描述的词语!是哪个版本的? [s:90] [s:90] |
|