标题: BS1363问题 [打印本页] 作者: kingport 时间: 2011-11-16 23:03 标题: BS1363问题 现我遇到下列问题,望知道的大哥帮忙解决一下。 " \* }2 l2 ]. p& y7 P! d关于BS1363/ 0,75 1,0 /配3A 5A 10A 13A 是参照BS1363哪一点。 9 c* u1 ?1 e0 X# l& Q2 z+ a3 H怎么配的。作者: shenhao168 时间: 2011-11-17 08:25
看一下BS1363 -2 table2,不知是不是要这个。作者: hugohugohugo 时间: 2011-12-16 12:54
要看ADG07 OR 14作者: aji 时间: 2011-12-19 11:02
LZ指的是配的fuse,那就看table 2作者: glen 时间: 2011-12-19 11:53
We can try to explain what is permitted by BS 1363-1, even if we cannot always give the reasons for the requirements.# I) M5 o8 {1 j# t
Table 2 describes the maximum plug ratings according to the size of cord fitted. % T2 \+ e) Q! ^" Y! bThe usual maximum rating when fitted with 0.75mm cord is 6 Amperes. : Y3 v+ F. }+ }- F- gA rating of 10 Amperes can be assigned, provided that the cord length is no more than 2 metres and the parameters for testing at 10 Amperes are used. These are more onerous than for 6A. ( v1 S( m! r/ T0 }" ~6 KThe test parameters used during testing of your samples were appropriate to the usual rating of 6A. ; Z! F5 n9 b+ @$ v # C9 E# e; _9 s5 W1 |! x, [2 ~9 YThe purpose of the fuse in the plug is to protect the cord, not the appliance which the cord is connected to. " N; |5 D' T M( q! N" XTable 2 gives the maximum rating of fuse according to the plug rating.6 l! P/ U2 ]. o S
It allows fuses up to 13A to be used with plugs rated 6A, 10A or 13A. 0 D" ]! D) J/ u, n3 OThe plug must be marked with the rating of the fuse link fitted. 1 k0 v: w O( k) M
This means that your plugs with 0.75mm cord are rated 6A but could have a 13A fuse and be marked 13A, but they must not be supplied for use where the rms current exceeds 6A.: u4 Y) y, ~* D5 u+ D
(An initial higher current such as for motor starting is permitted).+ W: ]. Z, u& ~
The plugs could have lower rated fuses but the marking must always show the rating of fuse fitted.1 Z! q3 }! S9 R" D
Appliance manufacturers may have a preference for the size of fuse.作者: kingport 时间: 2011-12-25 22:07
谢谢,只可惜是英文的,看不懂。要是中文的就好了。